I am not 100% sure. I think if I’m right it might be a problem for people with already created models only.
With another one I just tried and there are no issues.
I know that we added this check within the last month or so since EnergyPlus will complain if adjacent Faces don’t have constructions in reversed order from one another. This is why the best practice when developing ConstructionSets is to make the interior floor construction with reversed layers from the interior ceiling. It’s also why it’s a good idea to have interior wall constructions be symmetric (eg. gypsum, air gap, gypsum) so that they are always in reversed order from each other.
Are you using ConstructionSets to assign your constructions, @martin6 ? Or do you have constructions assigned on a Face-by-Face basis?
I’m getting this validation error currently: I just did a fresh PO dev version install an hour or two ago:
Using the built in construction sets: assigned via selecting all rooms and using edit in the PO toolbar:
it was with a model created via an older install of PO app.
Edit/Update:
It looks like the root cause was some geom discrepancies effecting proper adjacencies: Problem in chair not equipment
Side note: the newest update for the PO app: 10/10! super awesome great work and many thanks!